Fluke
  • Fluke
Fluke
Blog Fixing Irregular Batch Weights at a Food Processor
Join Fluke to participate - click to join for free!
  • Author Author: Amy_Fluke
  • Date Created: 25 Jan 2010 10:06 PM Date Created
  • Views 886 views
  • test
  • scope
  • 199b/s
  • scopemeter
  • meter
  • tool
  • fluke
Amy_Fluke
Amy_Fluke
25 Jan 2010
The process: Weighing and dense phase conveying of batches of grain.
The scale: Mettler Toledo 8510
The meter: Fluke 199B/S ScopeMeterRegistered test tool
A vessel on three load cells is filled from a hopper above with around 1500 pounds of grain, depending on the recipe. The slide gate metering the grain is controlled by a PLC-5 based on weight read from the scale terminal. The vessel pressurizes and the grain is forced out the bottom into a transport pipe, sending the grain across the building to processing. When empty, a blower purges the line.
We were getting irregular batch weights. The weight indicated on a Wonderware terminal would occasionally jump low. The weight shown on the scale display was stable. The 4-20mA signal from the scale to the PLC seemed stable with a Fluke 179 Digital Multimeter. Another signal connected to the same channel seemed stable, but that was done with the system idle. Another channel then another input module was tried. Any problem could not readily be seen looking at raw data in RS Logix.
I requested and got the CS20MA for my new toy, the Fluke 199B. I connected in series and recorded a batch. The first batch recorded showed no obvious signs of trouble. Filling and discharging weight seemed smooth although the empty current was a little low.
Seen above: The slide gate opens, the scale fills, the slide gate closes. After stabilizing, the gate cycles one more short time to top off the batch. Compressed air empties the scale.
The next batch was a scope record:
That sure didn't look right. The noise at the end is the blower running but why was the signal 3-7mA thick?
Zooming in on the noise:
The frequency measuring feature saved me some math. After seeing the dips at 120 Hz, I was sure there was a bad capacitor after a bridge rectifier somewhere.
I consulted the scale manual. The interconnect diagrams on pages 58-59 showed me that the analog output module on the back of the scale got 120VAC in and the loop power originated on board. Page 55 shows the analog board. C8 and C10 are 470uF 35V. C9 between them is 47uF 25V. Radio Shack actually stocked these caps in 35 V. The 47uF C9 was the culprit. I replaced all three caps for four bucks.
Here's the clean signal with new caps:
When the PLC sampled the analog data, some data reads would be in the dips, giving us erroneous readings. The Fluke ScopeMeter made this easy to find.