RoadTest: VeriSafe Panel-Mtd. Voltage Tester
Author: Robert Peter Oakes
Creation date:
Evaluation Type: Test Equipment
Did you receive all parts the manufacturer stated would be included in the package?: True
What other parts do you consider comparable to this product?: It is designed to replace a safety procedure involving a cat III or cat IV multi-meter and a very time tested process to verify is a piece of equipment is safe to work on, by what can be simply described as verifying there is no voltage present and therefor the worker is not in harms way. So I guess a Multi-meter and a process is the comparable product.
What were the biggest problems encountered?: The Biggest problem was the fact the device literally told me the circuit was safe when in fact 110V AC was present on the device, This represents a BIG FAIL as this device is a critical safety product.
Detailed Review:
The Road Test in this case is pretty straight forward given the nature of this product. Why Would you use it, How do you use it and Does it work
So people dont have to read all of the road test to find this out, I was able to show a scenario were the A.O.V. Tester failed to report 110V AC still connected to it, it showed a GREEN SAFE indication, this was with a wiring fault (Deliberate) but this still should not have given the all clear. Now please read on.
The VeriSafe Panel-Mtd. Absence of Voltage Tester is a device intended for industrial use but could also be used domestically or in small office or commercial spaces.
When people work in electrically hazardous environments it is standard practice (REQUIRED) to power down equipment prior to working on that equipment and perform absence of voltage tests before starting work. This is in order to provide a safe environment for the worker, often this is not very convenient but it should never be neglected or omitted,
The process to validate the power is isolated from the equipment to be worked on is fairly straight forward
1. Select a working and suitably rated multi-meter
this is NOT a suitable meter or the correct way to use it.... can you tell me why???
A suitable meter will have a known brand and a trusted certification, CE is not enough, that can be self applied by any manufacturer, Any multi-meter that has Amps and Volts on the same jack, or even a transistor tester built in would NOT be suitable in my opinion, your life is not worth it., in the picture above the circuit is about to be tested and the user has a transistor left in the socket... that will be ok right!!!!, oh and did I mention the long UN-insulated probes just waiting to short out something, may be necessary in some scenarios but CAT Rating also requires probe covers of the right type be correctly fitted in order to be valid..
2. Validate the meter is reading correctly, especially for the voltage your testing for, or more specifically the voltage your hoping will not be present... what if it is still there!
3. Test the circuit your going to be working on to ensure the voltages normally there are not and that in fact there are no unsafe voltages present.
4. Re-Test your meter to ensure it is still working correctly, this double validation is critical, especially if your working in CAT IV where you can have many phases and 415VAC or more present, if you accidentally popped the fuse in your meter and did not realize it, you could be in trouble
5. Now if the process provided the results you need, proceed with the work... simple right, sure but tedious but still essential for personal safety.
The VeriSafe Panel-Mtd. Absence of Voltage Tester is designed to be installed into a panel or other electrical installation in a way that will detect the hazardous voltages normally present in the equipment, the indicator is through hole mount so should be mounted on a suitable panel or fascia.
The nice thing with this unit is that it will work for DC voltages as well as AC Voltages, the down side is that in DC mode, the RED phase live indicators do not illuminate, they do for AC Mains though.
The Green "SAFE" indication works for both AC and DC voltages and will detect any voltage exceeding 3V across any of the color sets including to ground. I tested this to my satisfaction.
For redundancy and additional pre and post testing when you start a test, there are two sense wires for each connection, the idea is that you will connect them to the monitored point with separate connections... like so:-
This picture from a Panduit video demonstrates the desire for two separate connection to the circuit to be monitored but I am not so sure about the seriously exposed metal work there with 415V 30A power potentially, but later it shows then heavily taped up.
Also in the video it clearly states (At 3:23) that if a sense wire is not connected correctly then it will present a warning result, as you will see in my video, this is not always the case!,
I demonstrate a scenario in the video where the sense wire was disconnected but either touched another powered down phase wire or simply a low impedance path to ground (1.7K is the measured resistance of my multi-meter in low Z mode). I still had 110V AC connected to the other pair of the sense wire (Brown wire in this test), when I pushed the test button it actually showed a GREEN SAFE condition but I knew this was not the case.... now I will never trust it 100%.
To be fair, as long as the wiring is intact or if the broken/disconnected sense wire is not touching anything else then it gives a correct reading, unfortunately real life is not always like that so be warned and look at the wiring every now and again if your using one of these. On the flip side though, this is trying to get you to skip the manual process and trust it is looking out for you so are you willing to put your life in its hands knowing what I have just said ?
ok, so in summary, I like what the tester is trying to achieve but given the scenario I discovered where it reports incorrectly, I would never recommend the use of this in any critical application, and would still recommend some manual checks even if this is installed. There could be some situations were the risk of this occurring is minimal and therefor acceptable but I cant think of any right now.
Here is the videos
Part 1 looks at the unit and its operation, Part 2 I perform some actual live testing of the AOV Tester, be sure to check out time index 12:45 and 16:20 for unfortunate surprises
Top Comments
Interesting review. I forwarded it to my bosses and it's been forwarded to the supplier. What I was told is the supplier is examining the things that Peter pointed out. I expect they will respond promptly…
I like this interaction between testers and manufacturers. Everyone gains from that.
Great review, superb find out on the operation of it, well done.
I would also add that 500mA fused test leads are not being utilised in the multi-meter photo amongst the other faults visible. In my industry…