element14 Community
element14 Community
    Register Log In
  • Site
  • Search
  • Log In Register
  • About Us
  • Community Hub
    Community Hub
    • What's New on element14
    • Feedback and Support
    • Benefits of Membership
    • Personal Blogs
    • Members Area
    • Achievement Levels
  • Learn
    Learn
    • Ask an Expert
    • eBooks
    • element14 presents
    • Learning Center
    • Tech Spotlight
    • STEM Academy
    • Webinars, Training and Events
    • Learning Groups
  • Technologies
    Technologies
    • 3D Printing
    • FPGA
    • Industrial Automation
    • Internet of Things
    • Power & Energy
    • Sensors
    • Technology Groups
  • Challenges & Projects
    Challenges & Projects
    • Design Challenges
    • element14 presents Projects
    • Project14
    • Arduino Projects
    • Raspberry Pi Projects
    • Project Groups
  • Products
    Products
    • Arduino
    • Avnet Boards Community
    • Dev Tools
    • Manufacturers
    • Multicomp Pro
    • Product Groups
    • Raspberry Pi
    • RoadTests & Reviews
  • Store
    Store
    • Visit Your Store
    • Choose another store...
      • Europe
      •  Austria (German)
      •  Belgium (Dutch, French)
      •  Bulgaria (Bulgarian)
      •  Czech Republic (Czech)
      •  Denmark (Danish)
      •  Estonia (Estonian)
      •  Finland (Finnish)
      •  France (French)
      •  Germany (German)
      •  Hungary (Hungarian)
      •  Ireland
      •  Israel
      •  Italy (Italian)
      •  Latvia (Latvian)
      •  
      •  Lithuania (Lithuanian)
      •  Netherlands (Dutch)
      •  Norway (Norwegian)
      •  Poland (Polish)
      •  Portugal (Portuguese)
      •  Romania (Romanian)
      •  Russia (Russian)
      •  Slovakia (Slovak)
      •  Slovenia (Slovenian)
      •  Spain (Spanish)
      •  Sweden (Swedish)
      •  Switzerland(German, French)
      •  Turkey (Turkish)
      •  United Kingdom
      • Asia Pacific
      •  Australia
      •  China
      •  Hong Kong
      •  India
      •  Korea (Korean)
      •  Malaysia
      •  New Zealand
      •  Philippines
      •  Singapore
      •  Taiwan
      •  Thailand (Thai)
      • Americas
      •  Brazil (Portuguese)
      •  Canada
      •  Mexico (Spanish)
      •  United States
      Can't find the country/region you're looking for? Visit our export site or find a local distributor.
  • Translate
  • Profile
  • Settings
Experts, Learning and Guidance
  • Technologies
  • More
Experts, Learning and Guidance
Ask an Expert Forum Connect 2 different wire gauge; is the smaller gauge affecting the capacity of the bigger wire gauge?
  • Blog
  • Forum
  • Documents
  • Leaderboard
  • Files
  • Members
  • Mentions
  • Sub-Groups
  • Tags
  • More
  • Cancel
  • New
Join Experts, Learning and Guidance to participate - click to join for free!
Actions
  • Share
  • More
  • Cancel
Forum Thread Details
  • State Suggested Answer
  • Replies 7 replies
  • Answers 5 answers
  • Subscribers 291 subscribers
  • Views 22068 views
  • Users 0 members are here
Related
See a helpful answer?

Be sure to click 'more' and select 'suggest as answer'!

If you're the thread creator, be sure to click 'more' then 'Verify as Answer'!

Connect 2 different wire gauge; is the smaller gauge affecting the capacity of the bigger wire gauge?

maolemieux
maolemieux over 6 years ago

Hello, I would like first to thank anyone taking the time to read this or help. I was wondering how to calculate how many amp I can use by connecting 2 different wire gauge. I am on a 12v dc circuit and would ie to connect a 12v led module to a battery for a long distance. The led modules come with a 22 awg gauge cable from the factory. I would like to run it for a long distance to the power source (battery or power supply) I plan to use awg 16 wire connected to the led module so I can make a big distance safely. I will solder the awg 16 to the awg 22 of the led module. I usually know how to calculate the max amp that I can run for a single wire gauge by looking at spec of wire. However I am not sure if the 22 awg wire gauge from the led will limit my 16 awg? Is the 16 awg maximum amp capacity is limited by the 22 awg or will the 16 awg be able to use it's full amp capacity?

 

So to calculate how far I can get with the awg 16 can I just calculate the 22 awg capacity and add to the 16 awg capacity or I need to calculate the 16 awg capacity as if it was a 22 awg?

 

 

I am sorry my english is not great I live in montreal and speak french

 

Thank again for any help

cheers

  • Sign in to reply
  • Cancel

Top Replies

  • Gough Lui
    Gough Lui over 6 years ago +5 suggested
    Your question is an interesting one can be solved by a little bit of thought - but the short answer is that each gauge and type of wire has its own maximum current capacity (ampacity) and connecting the…
  • jw0752
    jw0752 over 6 years ago +3 suggested
    Hi Mao, It sounds like you have an interesting project. Can you tell us what the current draw of the LED module is? Also how far is the long distance that you refer to? One thing that you can do is to…
  • jw0752
    jw0752 over 6 years ago in reply to maolemieux +2 suggested
    Hi Mao, You can always trust the voltage drop and the current to tell you what is happening. You said that you had a 7% voltage drop at the load end. If you began with 12 volts this would mean a drop of…
Parents
  • Gough Lui
    0 Gough Lui over 6 years ago

    Your question is an interesting one can be solved by a little bit of thought - but the short answer is that each gauge and type of wire has its own maximum current capacity (ampacity) and connecting the two together does not change the fact that the 16AWG portion has its own maximum current rating and the 22AWG portion has its own maximum current rating. Both maximum current ratings must be respected.

     

    The long answer:

    There's actually two different issues which are being mixed together. The first that you have mentioned is maximum current carrying capacity (or ampacity) and this refers to the maximum current the cable is rated to carry so it doesn't cause damage to its insulation. This is not necessarily a good current level to operate at, because the second issue is cable resistance which causes a voltage drop. Lets say your long run is 20m with 16AWG wire with an 80 degrees C rated insulation. Its maximum current capacity is 19A. But if you tried to pass 19A through the cable, you would lose 10.01V (190W of heat) with only 1.99V remaining to power your device. So in most practical instances, your cable choice should be constrained by resistive losses rather than the cable current carrying capacity. However, you can size your cable protection to respect the maximum ampacity to avoid cable damage during fault conditions (i.e. use a 15A fuse for example).

     

    Knowing this, the ampacity of your 16AWG cable may be 19A and the ampacity of your 22AWG cable might be 8A. How does this affect things? Well to put it simply, the ampacity of each size of cable must be respected. Think of a home electrical distribution supply - the main supply from your utility comes through thick cables and may be fused at 100A (cable has an ampacity at least 100A). But this is then connected to your end circuits including power points and appliances through thinner wire - mostly with ampacity around 20-30A. This is why each circuit has its own fuse or circuit breaker protecting that branch from fault current induced damage. This is an instance where one thick cable is powering many appliances through a number of thinner wires.

     

    But it also means that say you run one 16AWG run from the battery to a central point (with a fuse rated appropriately), you can also run several 22AWG runs from this point outward (separately fused for the 22AWG wire) depending on the total load as long as the total current on the 16AWG section doesn't exceed its limit, the total current on each 22AWG section doesn't exceed its limit and you have sufficient voltage remaining to power your end device. In practice, if you are just powering one device, or you won't exceed the ampacity of the thinnest wire in the system, you could use a single fuse to protect the whole set - i.e. you use a 5A fuse with the whole system when 16AWG can handle up to 19A and 22AWG can handle up to 8A, this is always going to be safe, but on the downside, it means you might not be able to make the best use of the wire in case you might want to add loads later.

     

    Regardless, I doubt that the ampacity will cause a problem - it's more likely that the resistance in your wires will make it hard to high currents for run long distances especially at low voltages. Even to push 5A through a distance of 20m will require 9AWG or thicker according to this Voltage Drop Calculator, so to avoid losses, it's best to use as thick of a cable as possible to run the maximum distance. Otherwise, in specialist scenarios, it is possible to increase voltage and then decrease it again later, to reduce transmission losses but the conversion will itself introduce losses.

     

    - Gough

    • Cancel
    • Vote Up +5 Vote Down
    • Sign in to reply
    • Verify Answer
    • Reject Answer
    • Cancel
Reply
  • Gough Lui
    0 Gough Lui over 6 years ago

    Your question is an interesting one can be solved by a little bit of thought - but the short answer is that each gauge and type of wire has its own maximum current capacity (ampacity) and connecting the two together does not change the fact that the 16AWG portion has its own maximum current rating and the 22AWG portion has its own maximum current rating. Both maximum current ratings must be respected.

     

    The long answer:

    There's actually two different issues which are being mixed together. The first that you have mentioned is maximum current carrying capacity (or ampacity) and this refers to the maximum current the cable is rated to carry so it doesn't cause damage to its insulation. This is not necessarily a good current level to operate at, because the second issue is cable resistance which causes a voltage drop. Lets say your long run is 20m with 16AWG wire with an 80 degrees C rated insulation. Its maximum current capacity is 19A. But if you tried to pass 19A through the cable, you would lose 10.01V (190W of heat) with only 1.99V remaining to power your device. So in most practical instances, your cable choice should be constrained by resistive losses rather than the cable current carrying capacity. However, you can size your cable protection to respect the maximum ampacity to avoid cable damage during fault conditions (i.e. use a 15A fuse for example).

     

    Knowing this, the ampacity of your 16AWG cable may be 19A and the ampacity of your 22AWG cable might be 8A. How does this affect things? Well to put it simply, the ampacity of each size of cable must be respected. Think of a home electrical distribution supply - the main supply from your utility comes through thick cables and may be fused at 100A (cable has an ampacity at least 100A). But this is then connected to your end circuits including power points and appliances through thinner wire - mostly with ampacity around 20-30A. This is why each circuit has its own fuse or circuit breaker protecting that branch from fault current induced damage. This is an instance where one thick cable is powering many appliances through a number of thinner wires.

     

    But it also means that say you run one 16AWG run from the battery to a central point (with a fuse rated appropriately), you can also run several 22AWG runs from this point outward (separately fused for the 22AWG wire) depending on the total load as long as the total current on the 16AWG section doesn't exceed its limit, the total current on each 22AWG section doesn't exceed its limit and you have sufficient voltage remaining to power your end device. In practice, if you are just powering one device, or you won't exceed the ampacity of the thinnest wire in the system, you could use a single fuse to protect the whole set - i.e. you use a 5A fuse with the whole system when 16AWG can handle up to 19A and 22AWG can handle up to 8A, this is always going to be safe, but on the downside, it means you might not be able to make the best use of the wire in case you might want to add loads later.

     

    Regardless, I doubt that the ampacity will cause a problem - it's more likely that the resistance in your wires will make it hard to high currents for run long distances especially at low voltages. Even to push 5A through a distance of 20m will require 9AWG or thicker according to this Voltage Drop Calculator, so to avoid losses, it's best to use as thick of a cable as possible to run the maximum distance. Otherwise, in specialist scenarios, it is possible to increase voltage and then decrease it again later, to reduce transmission losses but the conversion will itself introduce losses.

     

    - Gough

    • Cancel
    • Vote Up +5 Vote Down
    • Sign in to reply
    • Verify Answer
    • Reject Answer
    • Cancel
Children
No Data
element14 Community

element14 is the first online community specifically for engineers. Connect with your peers and get expert answers to your questions.

  • Members
  • Learn
  • Technologies
  • Challenges & Projects
  • Products
  • Store
  • About Us
  • Feedback & Support
  • FAQs
  • Terms of Use
  • Privacy Policy
  • Legal and Copyright Notices
  • Sitemap
  • Cookies

An Avnet Company © 2025 Premier Farnell Limited. All Rights Reserved.

Premier Farnell Ltd, registered in England and Wales (no 00876412), registered office: Farnell House, Forge Lane, Leeds LS12 2NE.

ICP 备案号 10220084.

Follow element14

  • X
  • Facebook
  • linkedin
  • YouTube