DIY Test Equipment
  • DIY Test Equipment
DIY Test Equipment
Blog TLE94112 Interactive Testing Platform
Join DIY Test Equipment to participate - click to join for free!
  • Date Created: 26 Jul 2017 9:02 PM Date Created
  • Views 5225 views
  • Likes 10 likes
  • Comments 32 comments
  • dc motor
  • infineon
  • testing
  • diytestequipch
  • xmc1100
  • pwm
  • brushed motor
  • serial terminal
  • tle94112el_shield
  • test platform
balearicdynamics
balearicdynamics
26 Jul 2017
    • Introduction
  • The Project
    • Planning the Design
      • Testing motors
      • Control I/O
      • DC/DC Regulator
    • Design in practice
    • The Testing Platform
  • The Software
    • Software Design
    • 1. Main Sketch
      • Main loop() structure
        • Motors running status block
        • Serial parsing block
        • Analog reading block
      • Other functions in the main sketch
      • LCD layout
    • 2. MotorControl Class
      • MotorControl - Hardware control methods
      • MotorControl - High level methods
    • 3. Commands Description and Syntax
    • Direction control
      • Action commands
      • Duty cycle settings to PWM channels
      • PWM channel selection for duty cycle settings
      • Motor select for settings
      • Motor enable
      • PWM Frequency selector
      • Freewheeling mode motor(s) setting
      • Show all motors configuration
I am one of the road testers for the Infineon DC Motor Shield w/ TLE94112EL for Arduino and this project shows the testing platform I developed to test the features of the board shield, but it is also useful to test the DC motors performance, as well as other motor controller boards for Arduino.
According to me, carrying out a testing on the road of this platform based on the Infineon TLE94112 IC requires a versatile and flexible platform to make possible all the tests without building a lot of unreliable breadboarded stuff with loose wires. Moreover, in order to widen the range of possible tests making the platform reusable in the future you need to add only few extra components.
A full test of the TLE94112LE shield for Arduino based on this platform will be published in the Road Test section.
The Project
Planning the Design
The idea of making an interactive testing platform evolved as I progressed analyzing in depth the shield features on several Arduino compatible platforms: Arduino UNO R3 , Chipkit PI and the Infineon XMC1100 Boot . All these platforms were reliable with no t special issues by the TLE94112 shield; for the final development I opted for the Infineon board due the better ARM MCU, which is faster and with more available flash and RAM memory (ARM Cortex M0 32 bit, 16Kb high-speed RAM, 64Kb Flash memory) I should admit that the better performance of this board compared to the Arduino UNO kept as reference.
Testing motors
To create a reference for the test platform I chosen 6 brushed geared micro-motors with electrical characteristics included in the acceptable ranges of the TLE94112LE IC assembled together on an Aluminium square bar.
To that aim, I used cheap motors from Pimoroni with the following characteristics:
Free-run current @ 6V: 60mA (max 120mA) - in some conditions can generate an overcurrent that is useful to test the error registers of the TLE94112
Stall torque @6V: 2.5Kg/cm
Stall current @6V: 900mA (TLE94112LE max current per half-bridge is just 0.9A)
Gear ratio: 298:1
A small 3D printed object has been designed to make visible the rotation of the motors.
Control I/O
Using a terminal to control the shield seemed immediately the right choice as the available control options open a wide scenario of many motion possibilities. The problem arose when I saw that some status information and configuration updates need continuous and immediate feedback. To solve this problem, an LCD display has been added to the testing board.
DC/DC Regulator
To provide the right power supply to the TL94112 a separate power line has been set through a DC/DC power regulator.
Design in practice
The working version of the design evolved around the features of the board I have experienced during the first phase of the hardware testing growing its complexity. The images below show the most meaningful steps.
{gallery} Platform design evolution
The last element added to the testing platform is a 50K potentiometer connected to the analog port 0. That will be used by the software when you need to read dynamic values (e.g. the manual duty cycle). The diagram below shows the components connection.
The Software
The hard part was developing the software, that required a lot of revisions, 37 pushes on the GitHub repository, but nowat last it is available as Open Source under the LGPL 3.0 license: https://github.com/alicemirror/TLE94112LE
Software Design
The software is divided into functional blocks as listed below
  • Main Sketch: initialize and setup the system. The main loop controls the TLE94112 through the Arduino library (via SPI protocol on PINs 8 and 10), the analog input and the parser, the messaging via the serial terminal and the LCD display.
  • Commands: definition of all the serial commands response messages and all related to the parsing.
  • MotorControl: the class interfacing the (thanks to) Infineon TLE94112 Arduino library with the high-level methods used by the serial commands
We'll see them in detail in the next chapters.
1. Main Sketch
I tried to reduce as much as possible the definition of global variables and constants in the main sketch. The only pre-processor definitions in the TLE94112LE.ino are limited to the global flags driving thebehaviorr of the program in the mainLoop() and the symbolic constants definitions strictly related to the application logic to avoid confusion and better readability and making the MotorControl class fully reusable in other projects.
//! Max analog reading range with a 50K potentiometer
#define MAX_ANALOG_RANGE 1024
//! Min analog reading range with a 50K potentiometer
#define MIN_ANALOG_RANGE 0
//! Duty cycle analog read should be ignore (bypass the analog reading)
#define ANALOG_DCNONE 0
//! Duty cycle analog read should be assgined to DC min
#define ANALOG_DCMIN 1
//! Duty cycle analog read should be assgined to DC mAX
#define ANALOG_DCMAX 2
//! Duty cycle analog read should be assgined to DC manual reading
#define ANALOG_DCMAN 3
A special note about the preprocessor directive _SERIAL_ECHO:
#define _SERIAL_ECHO - all commands are echoed to the serial terminal as shown in the example below
Serial output
setting  all
Direction  ccw
setting  none
setting  m1+
PWM:  80
setting  dc80
set  accel
setting  dc100
#undef _SERIAL_ECHO - only wrong commands are notified on the serial terminal
Serial output
wrong command  'mindc'
The main loop control the logic of the application. It is organised in three functional blocks checked sequentially every cycle depending on the status of the top flags and the data availability on the serial port (Tx/Rx, Pin 0 and 1)
This block is checked only if the system status is running (start command). Every loop cycle when the motors are running it is checked for the presence of some error on the TLE94112LE registers and eventually errors are notified on the serial terminal
  // Check if at least one motor is running to test the error status
  // Note: It is possible to isolate the error status, if any,
  // for any motor. Here we make a simplification and check over
  // the motor without filtering
  isRunStatus = false;
  for(j = 0; j < MAX_MOTORS; j++) {
    if(motor.internalStatus[j].isRunning) {
      isRunStatus = true;
      j = MAX_MOTORS; // Force exit from loop
    } // check for running motors
  } // motors loop
  // If at least one motor is running check for diagnostic
  if(isRunStatus) {
    if(motor.tleCheckDiagnostic()) {
      //! Show the error star
      lcdShowError();
      motor.tleDiagnostic();
      lcdClearError();
If there are data available on the serial, the parser function parseCommand(String) is launched to check the command (or return a command error).
Serial commands are received as String terminated by CR=LF characters to be supported by any terminal or common serial connection. The last two terminating characters are removed before the string parsing.
All the commands and parser related strings are defined in the header file commads.h
There are three conditions that enable the reading of analog values:
  • ANALOG_DCMIN User is setting manually via the potentiometer the minimum duty cycle value for one of the three PWM channels
  • ANALOG_DCMAX User is setting manually via the potentiometer the maximum duty cycle value for one of the three PWM channels
  • ANALOG_DCMAN User can change manually via the potentiometer the current duty cycle value for the PWM channel(s) enabled for manual duty cycle
The main sketch also includes the functions to control the optional LED (on pin 12) and the LCD layout control functions.
LCD layout
For obvious size reasons the LCD shows several layouts depending on the conditions using a layout with abbreviations; whenever possible, more readable strings have been used. The shortened symbols used by the LCD are listed below:
  • M1, M2, M3, ... M6 Set the corresponding motor
  • M* Set all the motors with the same parameter
  • PWM[1] 80Hz, PWM[2]100Hz, PWM[3] 200Hz Set one of the three PWM channels (assigned to a fixed frequency)
  • CW/CCW Clockwise/Counterclockwise direction of the selected motor(s)
  • FreeWh+/FreeWh- FreeWheeling active enabled/disabled for the selected motor(s)
  • DCMin Minimum duty cycle value for the selected PWM channel(s)
  • DCMax Maximum duty cycle value for the selected PWM channel(s)
  • ena/dis Selected motor(s) set as enabled or disabled
  • Ramp Set acceleration and deceleration for the selected PWM channel(s)
  • Inst. Set instant starting for the selected PWM channel(s)
The gallery below shows and example of several LCD layouts
{gallery} LCD Layout examples
The MotorControl C++ class is pat of the software, uses the TLE94112 Arduino Library by Infineon and is built around the files motorcontrol.cpp, motorcontrol.h and motor.h (extra preprocessor definitions). The class itself is structured through two level methods.
For the complete methods of the class and full documentation refer to the software available on the GitHub repository
The hardware control method interfaces directly the features of the hardware shield exposed by the TLE94112 Arduino library.
MotorControl:: tleCheckDiagnostic(void)
MotorControl::tleDiagnostic(int motor)
MotorControl::tleDiagnostic()
Check the diagnostic status and send the corresponding error message to the serial terminal (if any)
MotorControl::motorConfigHBCCW(int motor)
MotorControl::motorConfigHBCW(int motor)
and others similar to configure half bridges direction and the other parameters, the PWM channel, duty cycle etc.
The hight level methods interfaces the commands calling recursively after filtering potential errors, This avoid internal problems or unexpected behaviours or hardware damages.
Every parser command call one of the high level commands of this class.
Excluding the potentiometer on the board all the controls are sent via terminal through a USB-to-serial connection. When the system is in running mode it can accept configuration commands that will be effective after a stop and start call.
If errors occur while the system is running these are shown in detail on the serial terminal and are notified on the LCD screen
The available commands are listed below:
Direction control
  • cw : clockwise rotation
  • ccw : counterclockwise rotation
  • accel : enable the acceleration when motor start
  • noaccel : disable the acceleration when motor start
Action commands
  • start : start all motors
  • stop : stop all motors
  • reset : reset the system to the default
  • dcmanual : Set the duty cycle value depending on the pot
  • dcauto : Set the duty cycle current limits
  • dcmin : Set the min duty cycle value via pot
  • dcmax : Set the max duty cycle value via pot
  • dcinfo : Shows the duty cycle range for the selected PWM channel
  • dc80 : Set the duty cycle to the PWM channel 80Hz
  • dc100 : Set the duty cycle to the PWM channel 100Hz
  • dc200 : Set the duty cycle to the PWM channel 200Hz
  • dcPWM : Set the duty cycle to all the PWM channels
  • all : Select and enable all motors
  • none : Disble all motors
  • m1 : select motor 1
  • m2 : select motor 2
  • m3 : select motor 3
  • m4 : select motor 4
  • m5 : select motor 5
  • m6 : select motor 6
Motor enable
  • m1+ : enable motor 1
  • m2+ : enable motor 2
  • m3+ : enable motor 3
  • m4+ : enable motor 4
  • m5+ : enable motor 5
  • m6+ : enable motor 6
  • 80 : PWM 80 Hz
  • 100 : PWM 100 Hz
  • 200 : PWM 200 Hz
  • fwactive : Fereewheeling active
  • fwpassive : Freewheeling passive
  • conf : Dump the current settings
For the last updates and revisions please follow the TLE94112LE on GitHub
(special thanks to antoricagno for text review)
    jw0752 over 9 years ago +5
    Hi Enrico, This was a great project. I will never ask you what you do in your free time as I doubt that you have any. I liked the way you color coordinated the test board for clarity. Thanks for all the…
    balearicdynamics over 9 years ago in reply to jw0752 +4
    Hey John! Thank you. I appreciate this very much As a matter of fact I miss acouple of coloured wires so I had to decide for a compromise as well as the motors wrappers; when I bought the bunch of "multicolored…
  • Workshopshed
    Workshopshed over 9 years ago +3
    >The hard part was developing the software. It required a lot of revisions, 37 push on the GitHub repository Yup software is hard. My projects seem to range from a tiny 8 commits through to the Enchanted…
  • wanfp97
    wanfp97 over 6 years ago
    Hi Enrico,
    I am recently dealing with the TLE94112 shield and I found this helpful post. I'm completely new on this, do you have any suggestions for me to learn how to control it using a XMC from Infineon?
    Fook Peng
    balearicdynamics over 6 years ago in reply to wanfp97
    Hello! Consider that the motor control works fine with both Arduino and the Infineon Arduino compatible platform. If you download the github repository I developed for this article, you find all the features in a sort of metalanguage, easy for testing and using the single methods for your application or just integrating your software with this tool.
    Enrico
  • wanfp97
    wanfp97 over 6 years ago in reply to balearicdynamics
    Thanks a lot Enrico. You really saved my day.
    Best Regards,
    Fook Peng
    Happy that my work is useful. If you need help of support on using&modifying it, just ask.
    Enrico
  • wanfp97
    There is one thing I'm curious about. How did you know what signal need to be sent to the motor control shield using SPI at the first place? I can't find the controlling signal in the datasheet. Did I overlook something?
    Fook Peng
    If you mean the chip select, it is hardware set via a jumper. The system can support up to two (or three I don't remember) stacked boards.
    If you mean something else, please explain that I have not understood.
    Enrico
  • wanfp97
    For example in the TLE94112LE.ino file, there are many Serial.<something>. I have tried to Google it and found that this calling a function from the Serial Class, but I didn't see Serial being attached to any Object. Is there some other header files that I have overlook?
    I have look through the motorcontrol.h file and found several function prototypes but didn't manage to find the declaration. Is it the Arduino IDE will include some other library that have the declarations for that? If yes, how do I include those library in my project?
    Sorry for asking so much questions and bothering you. Some of my questions may even sound stupid because I'm not really familiar with C++. Thank you for spending your time helping me.
    Sincerely,
    Fook Peng
  • wanfp97
    Sincerely,
    Fook Peng
    Hello Fook,
    if you load the project after cloning the repo, you see that the .ino is just the main architecture. This tested has a full set of serial controlled features that are defined in the dedicated class to make the code portable.
    In detail,
    • mtorcontrol.cpp defines all the API of the class to control the motor
    • commands.h header file instead includes the definition of all the textual commands that can be required from the serial (the USB serial terminal, and he Arduino Ide serial terminal are perfect)
    • motor.h header defines both the driver control parameters as well (to the bottom) the output strings that generates the serial interface
    In the main loop() of the ino sketch, the LCD display just shows the status to see what is happening, but for a detailed control you should use the serial commands that are designed to be sent by humans as well as by another computer controlling one or more driver up to one Arduino UNO and twelve motors.
      // BLOCK 2 : SERIAL PARSING
      // Serial commands parser
      if(Serial.available() > 0){
        parseCommand(Serial.readString());
      } // serial available
    The above block in the loop() of the sketch just checks continuously if the user has sent a control command from the serial to the USB interface (the same desktop used to program the Arduino) and the command is parsed with a proper serial response.
    All this is anyway well described in this post. Check paragraph 3 Controller commands of this post above for a detailed explanation of all the commands.
    Enrico
  • wanfp97
    My bad, I misunderstood your project function. Anyway, I found another blog by you with the 3D printer filament automatic dispenser function and most likely is what I'm finding. I will go to that blogpost and start learning there. Thanks for helping me out. I have really learnt a lot from you.
    Fook Peng
    Hello Fook,
    as I wrote in reply to dubbie  a few lines below here,
    thanks to this fantastic controller to make the 3D printer filament dispenser project you can find here: 3D Printer Filament Automatic Dispenser for Arduino - #1 Design and Hardware
    The project (3 long posts) you found is just the real-world application I have done using the tool described in this post.
    Enrico
  • wanfp97
    Hi Enrico,
    Fook Peng here again. I faced some difficulties when trying to control dc motors using the TLE94112EL.
    For the DC Motor Shield with TLE94112EL, the user manual state that we should communicate with it using SPI.
    when I'm trying to send the controlling signal from XMC4700 using SPI Master with the below codes nothing happens
    These are the binary to unsigned decimal conversion for your convenience:
    image image
    Did I do something wrongly?
    PS: I have connected the dc motor to out1 and out2 of the DC Motor Shield
    Regards
    Fook Peng
  • wanfp97