element14 Community
element14 Community
    Register Log In
  • Site
  • Search
  • Log In Register
  • Community Hub
    Community Hub
    • What's New on element14
    • Feedback and Support
    • Benefits of Membership
    • Personal Blogs
    • Members Area
    • Achievement Levels
  • Learn
    Learn
    • Ask an Expert
    • eBooks
    • element14 presents
    • Learning Center
    • Tech Spotlight
    • STEM Academy
    • Webinars, Training and Events
    • Learning Groups
  • Technologies
    Technologies
    • 3D Printing
    • FPGA
    • Industrial Automation
    • Internet of Things
    • Power & Energy
    • Sensors
    • Technology Groups
  • Challenges & Projects
    Challenges & Projects
    • Design Challenges
    • element14 presents Projects
    • Project14
    • Arduino Projects
    • Raspberry Pi Projects
    • Project Groups
  • Products & Partners
    Products & Partners
    • Arduino
    • Avnet & Tria Boards Community
    • Dev Tools
    • Manufacturers
    • Multicomp Pro
    • Product Groups
    • Raspberry Pi
    • RoadTests & Reviews
  • About Us
    About the element14 Community
  • Store
    Store
    • Visit Your Store
    • Choose another store...
      • Europe
      •  Austria (German)
      •  Belgium (Dutch, French)
      •  Bulgaria (Bulgarian)
      •  Czech Republic (Czech)
      •  Denmark (Danish)
      •  Estonia (Estonian)
      •  Finland (Finnish)
      •  France (French)
      •  Germany (German)
      •  Hungary (Hungarian)
      •  Ireland
      •  Israel
      •  Italy (Italian)
      •  Latvia (Latvian)
      •  
      •  Lithuania (Lithuanian)
      •  Netherlands (Dutch)
      •  Norway (Norwegian)
      •  Poland (Polish)
      •  Portugal (Portuguese)
      •  Romania (Romanian)
      •  Russia (Russian)
      •  Slovakia (Slovak)
      •  Slovenia (Slovenian)
      •  Spain (Spanish)
      •  Sweden (Swedish)
      •  Switzerland(German, French)
      •  Turkey (Turkish)
      •  United Kingdom
      • Asia Pacific
      •  Australia
      •  China
      •  Hong Kong
      •  India
      •  Japan
      •  Korea (Korean)
      •  Malaysia
      •  New Zealand
      •  Philippines
      •  Singapore
      •  Taiwan
      •  Thailand (Thai)
      •  Vietnam
      • Americas
      •  Brazil (Portuguese)
      •  Canada
      •  Mexico (Spanish)
      •  United States
      Can't find the country/region you're looking for? Visit our export site or find a local distributor.
  • Translate
  • Profile
  • Settings
RoadTests & Reviews
  • Products & Partners
  • More
RoadTests & Reviews
Review Blogs MIT420/2 Insulation Tester Review Blog 10 - Retest of 120MW Generator Rotor Winding
  • Blogs
  • Forum
  • Documents
  • RoadTests
  • Reviews
  • Polls
  • Files
  • Members
  • Sub-Groups
  • More
  • Cancel
  • New
Join RoadTests & Reviews to participate - click to join for free!
  • Share
  • More
  • Cancel
  • Author Author: three-phase
  • Date Created: 5 Jan 2018 9:59 AM Date Created
  • Views 3517 views
  • Likes 5 likes
  • Comments 10 comments
Related
Recommended
  • mit420/2
  • megger
  • insulation test
  • road test
  • thermocouple_measurement

MIT420/2 Insulation Tester Review Blog 10 - Retest of 120MW Generator Rotor Winding

three-phase
three-phase
5 Jan 2018

During my review of the Megger  MIT420/2MIT420/2 insulation tester in Blog 9, I tested a 120MW Generator rotor winding that actually failed the insulation resistance test. Following this issue, the bedplate heaters for the generator were reconnected and placed back into service. Around 4 weeks later, I returned to the generator to carry out a further insulation test with the expectation that the heat would have driven out the moisture from the winding and a healthy insulation reading would be obtained.

 

image

 

With the heaters being disconnected during the last test, the winding temperature was taken as being the same as the ambient temperature. With the heaters in service, a higher winding temperature was expected and this was verified by measuring the resistance of the embedded winding temperature sensors. These are PT100 devices and tables are easily obtainable to cross reference the resistance obtained to a temperature value.

 

The resistance measured cross referenced to 21 degrees Centigrade which is circa 10 degrees above the ambient conditions. To maintain the winding in preservation, the recommendations are to maintain the winding temperature 5 degrees above the ambient and the humidity below 30% RH.

 

Initially the resistance was measured with the resistance function on the Megger  MIT420/2MIT420/2 However it was found that the resistance value in excess of 100 ohms was set to a scale without any decimal places This introduces a slight inaccuracy when using the insulation tester for this test For the purposes of an insulation test this isn't an issue but when measuring the winding resistance the corrected value can be affected due to the inaccurate temperature correction as detailed in the video below(lasts 1m 45s

 

You don't have permission to edit metadata of this video.
Edit media
x
image
Upload Preview
image

 

A comparison of the rotor winding resistances obtained can also be seen in the table below.

 

image

 

For this reason the winding temperature sensor resistance was measured with the Keysight  U1461AU1461A to obtain a more accurate value In fairness to the Megger I don't think it was ever designed to replace the resistance function on a multi-meter Even the Keysight  U1461AU1461A only displayed one decimal place for the scale so a good multi-meter would generally offer an extra digit over this as well

 

The 1 minute insulation resistance test was conducted at 250V and then 365V using the variable voltage function of the Megger  MIT420/2MIT420/2 This setting was used to match the working voltage rating of the rotor winding A final test was then recorded at 500V

 

image

When carrying out multiple insulation tests at different voltages, the expectation would be to see a drop in insulation resistance as the voltage is increased. The results obtained didn't display this trait and this can sometime happen with large inductive apparatus when carrying out a succession of tests, as stored charges can sometimes remain and affect the next test result. This is resolved by allowing for longer discharge times between tests.

 

However, the values obtained during this set of tests were much better than the previous tests as shown in the comparison table below.

 

image

 

The DAR values were found to be above the minimum value of 1.2 for both the 365V and 500V tests, where as during the previous test they were around 1.00, which would be considered too low. The video of the instrument set-up on the variable voltage and the full DAR test is below and lasts circa 3 minutes.

 

You don't have permission to edit metadata of this video.
Edit media
x
image
Upload Preview
image

 

As such a good 1 minute insulation test value was obtained, the polarisation index test was conducted at 365V and then again at 500V to see if an increase in voltage would have an adverse effect on the insulation reading obtained.

 

imageimage

 

A good polarisation index value was obtained for both test voltages, 3.05 for the 365V test and 3.03 for the 500V test, well above the minimum value of 2.00. The insulation resistance plot seen above shows the classic response for a polarisation index test. This time the 500V test produces a slightly lower reading than the 365V test as expected. The drop however, is not significant enough to cause concerns.

 

The video below is the polarisation index test at 365V. I have sped up the test to reduce it down to around 4 minutes.

 

You don't have permission to edit metadata of this video.
Edit media
x
image
Upload Preview
image

 

Overall the  MIT420/2MIT420/2 continues to perform very well and I am happy to continue using it It has done around 300 tests to date of various types and the battery voltage drops down to 50 during the heavier current tests so appears to have a reasonable life

  • Sign in to reply

Top Comments

  • three-phase
    three-phase over 8 years ago in reply to jw0752 +3
    Hello John, Thanks for the comments. Insulation testers are very easy to get hold of, I have often thought that I would like to get hold of a cheap unit to tear down for comparison to the likes of the…
  • jw0752
    jw0752 over 8 years ago in reply to three-phase +3
    Hi Donald, Thank you for taking the time to give me all the valuable supplemental information. It is really appreciated. I liked your little test box with the flexibility of the bar jumpers to change the…
  • jw0752
    jw0752 over 8 years ago in reply to Jan Cumps +3
    Hi Jan, Thanks for the link but it is too late for me. The one who will have the problem though is my poor wife who will have no clue what to do with all this (cool, awesome, wonderful, relevant, neat…
  • jw0752
    jw0752 over 8 years ago in reply to mcb1

    Hi Mark,

     

    Not a bad idea, I'll tell her about it.

     

    John

    • Cancel
    • Vote Up +1 Vote Down
    • Sign in to reply
    • More
    • Cancel
  • mcb1
    mcb1 over 8 years ago in reply to jw0752

    The one who will have the problem though is my poor wife who will have no clue what to do with all this (cool, awesome, wonderful, relevant, neat)  test equipment when I suddenly make my exit.

    New inclusion into your will .... send tickets to my friends at element14 to 'rehost' my workshop.image

     

    Mark

    • Cancel
    • Vote Up +3 Vote Down
    • Sign in to reply
    • More
    • Cancel
  • jw0752
    jw0752 over 8 years ago in reply to Jan Cumps

    Hi Jan,

     

    Thanks for the link but it is too late for me. The one who will have the problem though is my poor wife who will have no clue what to do with all this (cool, awesome, wonderful, relevant, neat)  test equipment when I suddenly make my exit.

     

    Save yourself !      If you can. image

     

    John

    • Cancel
    • Vote Up +3 Vote Down
    • Sign in to reply
    • More
    • Cancel
  • Jan Cumps
    Jan Cumps over 8 years ago in reply to jw0752

    jw0752  wrote:

     

    Hi Donald,

    Thanks for the nice report. Due to posts like yours I have gotten an interest in experimenting with a megger. A more or less inexpensive one is on my 2018 items to buy list.

    John

    there is a dedicated forum thread over at EEVblog for people that became test gear addicted because of another post image

    • Cancel
    • Vote Up +2 Vote Down
    • Sign in to reply
    • More
    • Cancel
  • jw0752
    jw0752 over 8 years ago in reply to three-phase

    Hi Donald,

     

    Thank you for taking the time to give me all the valuable supplemental information. It is really appreciated. I liked your little test box with the flexibility of the bar jumpers to change the configuration.

     

     

    John

    • Cancel
    • Vote Up +3 Vote Down
    • Sign in to reply
    • More
    • Cancel
>
element14 Community

element14 is the first online community specifically for engineers. Connect with your peers and get expert answers to your questions.

  • Members
  • Learn
  • Technologies
  • Challenges & Projects
  • Products
  • Store
  • About Us
  • Feedback & Support
  • FAQs
  • Terms of Use
  • Privacy Policy
  • Legal and Copyright Notices
  • Sitemap
  • Cookies

An Avnet Company © 2026 Premier Farnell Limited. All Rights Reserved.

Premier Farnell Ltd, registered in England and Wales (no 00876412), registered office: Farnell House, Forge Lane, Leeds LS12 2NE.

Follow element14

  • X
  • Facebook
  • linkedin
  • YouTube